My electrical wall outlets only have 87 volts by Boostdreamer
Started on: 05-07-2013 12:58 PM
Replies: 51
Last post by: Boostdreamer on 05-14-2013 10:11 AM
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 12:58 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
I was checking out a pair of 3-way switches in my living room that seemed to do nothing. I discovered that they control a single outlet. At least one is wired wrong and maybe one of the switches is bad but in discovering all of that I noticed that my outlet only shows 87 volts. I went and checked the other rooms upstairs and they are the same. This house was built in 1974.

Is it just me or is there a problem somewhere?

------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
PFF
System Bot
ray b
Member
Posts: 13946
From: miami
Registered: Jan 2001


Feedback score: N/A
Leave feedback





Total ratings: 326
Rate this member

Report this Post05-07-2013 01:06 PM Click Here to See the Profile for ray bSend a Private Message to ray bDirect Link to This Post
WELL YOU COULD PRAY TO THE LORD TO FIX IT

or call your landlord [more effective]

87v to ground or the other leg ? ie white to black wire or green ?
IP: Logged
ray b
Member
Posts: 13946
From: miami
Registered: Jan 2001


Feedback score: N/A
Leave feedback





Total ratings: 326
Rate this member

Report this Post05-07-2013 01:12 PM Click Here to See the Profile for ray bSend a Private Message to ray bDirect Link to This Post

ray b

13946 posts
Member since Jan 2001
check if you have aluminum wires
if you do you have a fire waiting to happen

you need to rewire with copper

also check if you have 110/120v at the fuse/breaker box before the wires
IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 01:12 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
 
quote
Originally posted by ray b:

WELL YOU COULD PRAY TO THE LORD TO FIX IT

or call your landlord [more effective]

87v to ground or the other leg ? ie white to black wire or green ?


I have the feeling that the Lord wants me to work on this one!

No landlord either, it's mine. I've only been here 2 years. Was my wife's before we were married.


------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
Red88FF
Member
Posts: 7793
From: PNW
Registered: Jan 2006


Feedback score: N/A
Leave feedback





Total ratings: 130
Rate this member

Report this Post05-07-2013 01:21 PM Click Here to See the Profile for Red88FFSend a Private Message to Red88FFDirect Link to This Post
 
quote
Originally posted by Boostdreamer:


I have the feeling that the Lord wants me to work on this one!

No landlord either, it's mine. I've only been here 2 years. Was my wife's before we were married.


Call the power company, there is most likely problem with the line in. I would guess transformer problem. This will F up electronics, Power tools and appliances so I would not wait.

Oh, try a different meter first.
IP: Logged
Wichita
Member
Posts: 20696
From: Wichita, Kansas
Registered: Jun 2002


Feedback score: N/A
Leave feedback





Total ratings: 326
Rate this member

Report this Post05-07-2013 01:25 PM Click Here to See the Profile for WichitaSend a Private Message to WichitaDirect Link to This Post
You probably have a neutral wire out or loose. Most likely this is the neutral bar breaking loose in the meter box.

IP: Logged
MadMark
Member
Posts: 2935
From: Owosso, Michigan, USA
Registered: Feb 2010


Feedback score: (4)
Leave feedback

Rate this member

Report this Post05-07-2013 01:30 PM Click Here to See the Profile for MadMarkSend a Private Message to MadMarkDirect Link to This Post
I agree with Witchita here. Check for loose neutral wires in the circuit.

One other thing to check to ensure you don't have a transformer problem is to check the voltage across the terminals on the power lead to your fuse/breaker box. You should have about 120 VAC to ground or neutral from any of the black wires coming in. And between the two black wires coming in you should have about 230-240 VAC.

If you don't feel comfortable working on it, get someone qualified to work on it.
IP: Logged
rogergarrison
Member
Posts: 49601
From: A Western Caribbean Island/ Columbus, Ohio
Registered: Apr 99


Feedback score: N/A
Leave feedback





Total ratings: 551
Rate this member

Report this Post05-07-2013 01:32 PM Click Here to See the Profile for rogergarrisonSend a Private Message to rogergarrisonDirect Link to This Post
 
quote
Originally posted by ray b:

check if you have aluminum wires
if you do you have a fire waiting to happen

you need to rewire with copper

also check if you have 110/120v at the fuse/breaker box before the wires


^^^^^^
This is my suggestion too. My parents built a new house in the early 70s. It had aluminum wire and nothing but problems from day one.

IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post05-07-2013 01:33 PM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
You definitely have a problem somewhere, or a combination of several problems. Check the voltage at the breaker panel. Actually, I guess the first thing would be to make sure you're using a good meter and that it's giving you an accurate reading. 87 is *really* low. i.e. if it's a battery operated digital meter, try replacing the battery too, just to be sure.

Meter each leg to ground where it comes into the panel. I would check each leg as is, then turn all the breakers off. Have an alternate light source ready, obviously. Meter incoming voltage with no load. If it's low then, there's a problem with the utility, or with your service entrance. If it checks okay with no draw from the house, then restore each breaker one by one to see if there's an obvious problem with one or two circuits so you can narrow your search.

What type of construction? We have a manufactured home. One of the things I did soon after we bought it was replace the cheap, worthless quick-connect splices where the wiring goes from one side of the house to the other. Put up a big J-box and used real wire nuts, and labeled all the wires in the process. We also had voltage issues due to the service. When the home was set, the utility put a pole-mounted transformer at the road and then had a run of about 500 feet to get to the meter, plus another 76 feet inside to get to the box. They looked at it and said it never should have been installed that way to begin with, ran new service underground and put a transformer much closer to the house.
IP: Logged
84fiero123
Member
Posts: 29950
From: farmington, maine usa
Registered: Oct 2004


Feedback score: N/A
Leave feedback





Total ratings: 325
Rate this member

Report this Post05-07-2013 01:34 PM Click Here to See the Profile for 84fiero123Send a Private Message to 84fiero123Direct Link to This Post
 
quote
Originally posted by MadMark:

I agree with Witchita here. Check for loose neutral wires in the circuit.

One other thing to check to ensure you don't have a transformer problem is to check the voltage across the terminals on the power lead to your fuse/breaker box. You should have about 120 VAC to ground or neutral from any of the black wires coming in. And between the two black wires coming in you should have about 230-240 VAC.

If you don't feel comfortable working on it, get someone qualified to work on it.


as do i.

check other outlets voltage, if they are different cances are it is just the ground for that outlet, not something to call the power company about, unless they all have lower voltage and it is not just a loose wire.

steve

------------------
Technology is great when it works,
and one big pain in the ass when it doesn't



Detroit iron rules all the rest are just toys.

IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 01:43 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
 
quote
Originally posted by AndyLPhoto:

What type of construction? We have a manufactured home. One of the things I did soon after we bought it was replace the cheap, worthless quick-connect splices where the wiring goes from one side of the house to the other. Put up a big J-box and used real wire nuts, and labeled all the wires in the process. We also had voltage issues due to the service. When the home was set, the utility put a pole-mounted transformer at the road and then had a run of about 500 feet to get to the meter, plus another 76 feet inside to get to the box. They looked at it and said it never should have been installed that way to begin with, ran new service underground and put a transformer much closer to the house.


It is a stick-built brick and siding house. It is about 75 feet from the power pole on the road.


------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
PFF
System Bot
ray b
Member
Posts: 13946
From: miami
Registered: Jan 2001


Feedback score: N/A
Leave feedback





Total ratings: 326
Rate this member

Report this Post05-07-2013 02:04 PM Click Here to See the Profile for ray bSend a Private Message to ray bDirect Link to This Post
what volts do you read at the breaker box
what color are the wire strands not the cover the wires themselves
red/copper is good green is bad silver is very bad [alloy]
IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 02:33 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
 
quote
Originally posted by ray b:

what volts do you read at the breaker box
what color are the wire strands not the cover the wires themselves
red/copper is good green is bad silver is very bad [alloy]


I can't access the wires at the breaker box without removing the outter panel. I'm not comfortable doing that. I can't get a voltage reading there.

I've changed some light fixtures, etc and all the conductors have been solid copper, three-wire romex.


------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 02:38 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post

Boostdreamer

7175 posts
Member since Jun 2007
I checked the outlets downstairs. They showed 95 volts. I re-checked the upstairs ones. They are 95 also. I'm going to suspect the meter for now. Let me change batteries.

------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 02:44 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post

Boostdreamer

7175 posts
Member since Jun 2007
New batteries! Volts still at 95

------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
Ang84Indy
Member
Posts: 576
From: Ohio
Registered: Jul 2009


Feedback score:    (7)
Leave feedback

Rate this member

Report this Post05-07-2013 02:54 PM Click Here to See the Profile for Ang84IndySend a Private Message to Ang84IndyDirect Link to This Post
Only way to find where the problem is ( supply, or your house) is to open the panel. Do you know an electrician? It's bad if the problem is in the panel or somewhere in the house. Fire is a real possibility.
IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 03:00 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
 
quote
Originally posted by Ang84Indy:

Only way to find where the problem is ( supply, or your house) is to open the panel. Do you know an electrician? It's bad if the problem is in the panel or somewhere in the house. Fire is a real possibility.


That's what worried me into fixing my last problem. I had three switches controlling the same light in the stairway. They didn't work right so it bugged me. I finally got into it and they had used the wrong switches. I'm not completely impressed with the wiring in this house!


------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post05-07-2013 05:10 PM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
 
quote
Originally posted by Boostdreamer:

I can't access the wires at the breaker box without removing the outter panel. I'm not comfortable doing that. I can't get a voltage reading there.

I've changed some light fixtures, etc and all the conductors have been solid copper, three-wire romex.


Getting into the panel is really the only way to make sure if the problem is yours or the power company's. It's not that big a deal, but don't do it if you're not comfortable. One other thing you could try is to kill all the breakers on one side, plus any 220 breakers, then check voltages at the remaining outlets. Then do the same for the other side. That could help give some clues before tearing into the box. Alternately, if there happens to be a circuit with outlets close to the panel (better yet an outlet right below it on its own circuit) kill everything but that one, unplug anything else on the circuit, and check voltage.

When you have checked voltages, have you checked outlets from both legs? In other words, from circuits on both sides of the panel?

Other than that, get an electrician, or a friend who is a little more comfortable to dig into the panel.
IP: Logged
fierobrian
Member
Posts: 2976
From: aurora il 60505
Registered: Sep 2003


Feedback score: (1)
Leave feedback





Total ratings: 80
Rate this member

Report this Post05-07-2013 05:55 PM Click Here to See the Profile for fierobrianSend a Private Message to fierobrianDirect Link to This Post
i would shut the main braker down then take the cover over and turn power back and test it with a voltmeter . if the power is off while you take the cover off there is no chance of shorting anything it is ok to turn on with cover off everything will stay inplace . the cover is just a sheetmetal cover very thin piece of metal just to keep peaple from sticking finger in live wires .
IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post05-07-2013 06:40 PM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
Well, yes and no...even with the main breaker off, there is still live power coming into the box. It cuts it down to only two lugs with voltage, but they're about the biggest thing in the box too. It certainly cuts down on the number of places you can get burnt (so to speak) but you still have to be careful. The danger is minimal if you take it slow, and don't go poking around with your fingers--use a meter.
IP: Logged
Lilchief
Member
Posts: 1754
From: Vevay,Indiana
Registered: Feb 2004


Feedback score: (3)
Leave feedback

Rate this member

Report this Post05-07-2013 06:43 PM Click Here to See the Profile for LilchiefSend a Private Message to LilchiefDirect Link to This Post
If and when you test your panel for voltage make sure to test to the neutral lug and at the neutral wire it self. I had a similar problem at the meter base. Low voltage at the lug but good (120V) voltage on the incoming neutral wire. Problem loose wire and lug was ceased up/ corrodied. I had the Electric CO come fix it, I could have if they would have just killed the power at the top of the pole. Hot wires were too close for comfort.

------------------

85 GT 3.4
14.9 @ 90 1.9 60' Old TH125/3.06
Unknown New 4T60/3.42

IP: Logged
PFF
System Bot
Lilchief
Member
Posts: 1754
From: Vevay,Indiana
Registered: Feb 2004


Feedback score: (3)
Leave feedback

Rate this member

Report this Post05-07-2013 06:48 PM Click Here to See the Profile for LilchiefSend a Private Message to LilchiefDirect Link to This Post
Also make sure someone is there with you. They need to stand to the side and have a nonconductive item in case of an emergency.
IP: Logged
SCCAFiero
Member
Posts: 1144
From: Boca Raton, Fl USA
Registered: Apr 2006


Feedback score: N/A
Leave feedback

Rate this member

Report this Post05-07-2013 10:29 PM Click Here to See the Profile for SCCAFieroSend a Private Message to SCCAFieroDirect Link to This Post
Changing batteries for reading voltage probably wont matter. Meters use batteries more for ohm tests than anything else. What make and model meter are you using? How old is it? Hopefully not some $3 meter from Harbor Freight. Try unplugging and replugging the leads in several times to make sure they have a good connection. Are you comfortable removing an outlet from the wall and seeing if the wires were just pushed into the back of the outlet or if they are screwed to it. Measure the house voltage at your dryer or range outlet so you don't have to pull the cover off the panel.
Put your hand on the exposed parts of the circuit breakers and see if any of them are warm, they should be room temperature. Warm could be bad, hot is really bad.
IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-07-2013 11:07 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
I'm going to take the front panel of the box off tomorrow. Before I do that, I'm going to try the test where everything on one side of the box is off. Then the other side. My meter is a Craftsman model. Probably 10 years old but it has always been taken very good care of. It still looks like new. It has always performed well. It is digital. The continuity test works just fine. I've had switches and outlets pulled out. They have all had the conductors pushed in at the rear. Never connected to the side screws, except once. That time the wire was wrapped the wrong way around the screw. Idiots.

------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post05-07-2013 11:21 PM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
Make sure when you test either side, also turn off any 220 breakers, like for a range, well pump or water heater. Even though the breaker is physically only on one side, it draws from both legs. Then, if there are significant changes, you can also test with each 220 breaker back on individually. Good luck! Looking forward to hearing the results.
IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post05-07-2013 11:41 PM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post

AndyLPhoto

2420 posts
Member since Nov 2001
One follow-up comment. One thing I posted above was stated incorrectly, and misleading after I thought about it. I asked if you had checked voltages from outlets on both legs of the service, meaning both sides of the box. In reality, because of how the circuits are laid out, every other circuit on either side is opposite. i.e. the top left and top right are both on the same leg. The second one down on each side are on the opposite leg, and so on.

So turning off one side of the box doesn't kill everything on one leg, but it does take half the circuits out of the equation. As I mentioned above, also kill any 220 breakers (like a range, water heater, welder, well pump, etc.) because they are connected to both legs. If you've got the cover off, you can kill everything and measure what's coming into the panel. Again, looking forward to hearing your results!
IP: Logged
rogergarrison
Member
Posts: 49601
From: A Western Caribbean Island/ Columbus, Ohio
Registered: Apr 99


Feedback score: N/A
Leave feedback





Total ratings: 551
Rate this member

Report this Post05-08-2013 03:21 PM Click Here to See the Profile for rogergarrisonSend a Private Message to rogergarrisonDirect Link to This Post
Just as a backup check, take your meter and test a few friends houses voltage at their outlets. It would show if your meter is bad or if theres a general electric delivery problem.
IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-08-2013 05:48 PM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
I spent the day on the road running errands. Sill waiting on the wife to come home to be my firewatch. Stand by.

------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
jb1
Member
Posts: 2146
From: Tullahoma, Tennessee
Registered: May 2003


Feedback score: (3)
Leave feedback

Rate this member

Report this Post05-09-2013 03:22 AM Click Here to See the Profile for jb1Send a Private Message to jb1Direct Link to This Post
So it is every plug in the house? My father in-law had this problem with an apartment he built in his garage but it was only on one circuit of plugs... I tracked down to a loose neutral wire at the first plug in the circuit.. like someone suggested before.... No idea if it is every single plug in house... what about at the light switches?
IP: Logged
maryjane
Member
Posts: 70081
From: Copperas Cove Texas
Registered: Apr 2001


Feedback score: (4)
Leave feedback





Total ratings: 441
Rate this member

Report this Post05-09-2013 03:27 AM Click Here to See the Profile for maryjaneSend a Private Message to maryjaneDirect Link to This Post
 
quote
Originally posted by Wichita:

You probably have a neutral wire out or loose. Most likely this is the neutral bar breaking loose in the meter box.


This was the problem last time I had about 85V--neutral open.
IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-09-2013 09:25 AM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
 
quote
Originally posted by jb1:

So it is every plug in the house? My father in-law had this problem with an apartment he built in his garage but it was only on one circuit of plugs... I tracked down to a loose neutral wire at the first plug in the circuit.. like someone suggested before.... No idea if it is every single plug in house... what about at the light switches?


Every outlet I tried had the low voltage. I tested in 6 rooms. Upstairs and down. I tested one light switch. Same result. I have not gotten into the breaker box yet.


------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
PFF
System Bot
FriendGregory
Member
Posts: 4833
From: Palo Alto, CA, USA
Registered: Jan 2004


Feedback score: N/A
Leave feedback

Rate this member

Report this Post05-09-2013 07:13 PM Click Here to See the Profile for FriendGregorySend a Private Message to FriendGregoryDirect Link to This Post
 
quote
Originally posted by Boostdreamer:I have not gotten into the breaker box yet.

That is what we are waiting for. If the problem is before it gets to you, it is not your problem, it is the power companys. Confirm the problem, make a phone call.
IP: Logged
DeV8er
Member
Posts: 747
From: Oak Ridge MO
Registered: Oct 2004


Feedback score: N/A
Leave feedback

Rate this member

Report this Post05-10-2013 10:40 AM Click Here to See the Profile for DeV8erSend a Private Message to DeV8erDirect Link to This Post
Do I smell smoke? Get this repaired ASAP! I lost my home about 7 years ago due to faulty wiring.
IP: Logged
jaskispyder
Member
Posts: 21510
From: Northern MI
Registered: Jun 2002


Feedback score:    (22)
Leave feedback





Total ratings: 205
Rate this member

Report this Post05-10-2013 10:42 AM Click Here to See the Profile for jaskispyderSend a Private Message to jaskispyderDirect Link to This Post
 
quote
Originally posted by DeV8er:

Do I smell smoke? Get this repaired ASAP! I lost my home about 7 years ago due to faulty wiring.


I would be concerned with the motors and such in appliances.

IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-10-2013 10:45 AM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
Gonna open the box in a few hours when my wife gets home. She works half days on Friday so I'll be able to kill the lighs while still being able to see what I'm doing and have a responsible adult present "just in case".

------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
jaskispyder
Member
Posts: 21510
From: Northern MI
Registered: Jun 2002


Feedback score:    (22)
Leave feedback





Total ratings: 205
Rate this member

Report this Post05-10-2013 10:55 AM Click Here to See the Profile for jaskispyderSend a Private Message to jaskispyderDirect Link to This Post
 
quote
Originally posted by Boostdreamer:

Gonna open the box in a few hours when my wife gets home. She works half days on Friday so I'll be able to kill the lighs while still being able to see what I'm doing and have a responsible adult present "just in case".




So, she will be the one holding the broom, to pry you off the box?


IP: Logged
Boostdreamer
Member
Posts: 7175
From: Kingsport, Tennessee USA
Registered: Jun 2007


Feedback score:    (24)
Leave feedback





Total ratings: 98
Rate this member

Report this Post05-10-2013 10:58 AM Click Here to See the Profile for BoostdreamerSend a Private Message to BoostdreamerDirect Link to This Post
 
quote
Originally posted by jaskispyder:

So, she will be the one holding the broom, to pry you off the box?


That is my hope! Oh, crap! She's gonna see her Mother's Day present! I have two rocking chairs hidden in the garage!


------------------
Jonathan

Please join me in prayer that forum member Wichita gives his life to the Lord Jesus.
https://www.fiero.nl/forum/Forum6/HTML/100383.html
https://www.fiero.nl/forum/Forum2/HTML/121056.html

IP: Logged
jaskispyder
Member
Posts: 21510
From: Northern MI
Registered: Jun 2002


Feedback score:    (22)
Leave feedback





Total ratings: 205
Rate this member

Report this Post05-10-2013 11:08 AM Click Here to See the Profile for jaskispyderSend a Private Message to jaskispyderDirect Link to This Post
 
quote
Originally posted by Boostdreamer:


That is my hope! Oh, crap! She's gonna see her Mother's Day present! I have two rocking chairs hidden in the garage!



blindfold her and if you scream, she can take it off


IP: Logged
Purple86GT
Member
Posts: 1592
From: Ontario, Canada
Registered: Mar 2012


Feedback score: (1)
Leave feedback





Total ratings: 62
Rate this member

Report this Post05-10-2013 11:20 AM Click Here to See the Profile for Purple86GTSend a Private Message to Purple86GTDirect Link to This Post
Check for DC on the circuit. Neutral and ground go to the same circuit in the panel. If there is backfed DC in the circuit it would affect your voltage readings.

also, are these readings taken under load? (with the light on?) check if the readings change with the applicance (light, fan, whatever) on or off.

cheers!
IP: Logged
Phil
Member
Posts: 7034
From: Coventry, RI
Registered: Apr 99


Feedback score: (2)
Leave feedback





Total ratings: 154
Rate this member

Report this Post05-10-2013 12:25 PM Click Here to See the Profile for PhilSend a Private Message to PhilDirect Link to This Post
Just call the electric co - they'll come right out and check to see if you have the correct voltage coming into your house- No charge
IP: Logged
Previous Page | Next Page

This topic is 2 pages long:  1   2 


All times are ET (US)

T H I S   I S   A N   A R C H I V E D   T O P I C
  

Contact Us | Back To Main Page

Advertizing on PFF | Fiero Parts Vendors
PFF Merchandise | Fiero Gallery
Real-Time Chat | Fiero Related Auctions on eBay



Copyright (c) 1999, C. Pennock