Lilchief
Member
Posts: 1741
From: Vevay,Indiana
Registered: Feb 2004


Feedback score: (3)
Leave feedback

Rate this member

Report this Post06-18-2014 05:55 PM Click Here to See the Profile for LilchiefSend a Private Message to LilchiefEdit/Delete MessageReply w/QuoteDirect Link to This Post
I recently started working as a maintenance electrician and gave up on the construction field. The whole factory is an electrical mess. The issue I have came across is we have a 480V switch gear that has been changed to 208V. The fuses are rated at 600V instead of 250V. I've done several searches on line and tried to find something in the code book , no luck either way. I've thought about this in a light bulb senerio , like 6V bulb in a 12V system or the other way around 12V bulb in a 6V system. Maybe this senerio is not apples to apples. What's your ideas.
IP: Logged
PFF
System Bot
87antuzzi
Member
Posts: 11151
From: Surrounded by corn.
Registered: Feb 2009


Feedback score:    (9)
Leave feedback





Total ratings: 228
Rate this member

Report this Post06-18-2014 06:16 PM Click Here to See the Profile for 87antuzziSend a Private Message to 87antuzziEdit/Delete MessageReply w/QuoteDirect Link to This Post
How was it changed? Im going to assume they have 480 3 phase going to a step down with a wye secondary on the transformer to get the 120 line to neutral to run your 208 switch gear? I built this cabinet last night doing exactly that. This is taking 480 in, I tapped 2 legs and ran to the H1 and H4 on transformer and grounded x2 out to get my 208 output. But thats a single phase output. Is your 208 3 phase? Need more info.
This images is larger than 153600 bytes. Click to view.
IP: Logged
84fiero123
Member
Posts: 29950
From: farmington, maine usa
Registered: Oct 2004


Feedback score: N/A
Leave feedback





Total ratings: 325
Rate this member

Report this Post06-18-2014 06:28 PM Click Here to See the Profile for 84fiero123Send a Private Message to 84fiero123Edit/Delete MessageReply w/QuoteDirect Link to This Post
Forgive my stupid question, I am not an engineer or an electrician, but I always thought all 480 volt inputs were 3 phase. At least going into a commercial electrical system.

Steve

------------------
Technology is great when it works,
and one big pain in the ass when it doesn't



Detroit iron rules all the rest are just toys.

IP: Logged
87antuzzi
Member
Posts: 11151
From: Surrounded by corn.
Registered: Feb 2009


Feedback score:    (9)
Leave feedback





Total ratings: 228
Rate this member

Report this Post06-18-2014 06:35 PM Click Here to See the Profile for 87antuzziSend a Private Message to 87antuzziEdit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by 84fiero123:

Forgive my stupid question, I am not an engineer or an electrician, but I always thought all 480 volt inputs were 3 phase. At least going into a commercial electrical system.

Steve



They are. Without any info on how its stepped down im assuming he has a transformer thats stepping it down to a single phase output. If that IS the case then the 600v fuses are fine as long as its on the high side of the transformer. I like to run the control transformers on 1 amp mini fuses on the 2 hot legs coming in but I know people who dont because the main fuse is already there (sounds like the case here)
IP: Logged
Lilchief
Member
Posts: 1741
From: Vevay,Indiana
Registered: Feb 2004


Feedback score: (3)
Leave feedback

Rate this member

Report this Post06-18-2014 06:38 PM Click Here to See the Profile for LilchiefSend a Private Message to LilchiefEdit/Delete MessageReply w/QuoteDirect Link to This Post
It originally had a 480V 3ph coming in from the pole. At some point the transformer was changed to 208V 3ph 4w to first gear. It feeds a second gear that's rated 480V 3ph 3 w. Some idiot decided to use a ground rod to create a neutral. That has been changed now. Also many ungrounded circuits, as many as 7 circuits sharing one neutral. Just wondering about the fuse issue for now.

------------------

85 GT 3.4
14.9 @ 90 1.9 60' Old TH125/3.06
Unknown New 4T60/3.42

IP: Logged
87antuzzi
Member
Posts: 11151
From: Surrounded by corn.
Registered: Feb 2009


Feedback score:    (9)
Leave feedback





Total ratings: 228
Rate this member

Report this Post06-18-2014 06:52 PM Click Here to See the Profile for 87antuzziSend a Private Message to 87antuzziEdit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by Lilchief:

It originally had a 480V 3ph coming in from the pole. At some point the transformer was changed to 208V 3ph 4w to first gear. It feeds a second gear that's rated 480V 3ph 3 w. Some idiot decided to use a ground rod to create a neutral. That has been changed now. Also many ungrounded circuits, as many as 7 circuits sharing one neutral. Just wondering about the fuse issue for now.



600 volt is fine. The clearing times are the same same and the 600V rating is for the re-strike and insulation ratings. NEC says you can run a 600V gear on a 280V system, ill try to find the quotation. In a nut shell, you can run under rated voltage for fuses but never over.
IP: Logged
MadMark
Member
Posts: 2935
From: Owosso, Michigan, USA
Registered: Feb 2010


Feedback score: (4)
Leave feedback

Rate this member

Report this Post06-18-2014 11:24 PM Click Here to See the Profile for MadMarkSend a Private Message to MadMarkEdit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by 87antuzzi:


600 volt is fine. The clearing times are the same same and the 600V rating is for the re-strike and insulation ratings. NEC says you can run a 600V gear on a 280V system, ill try to find the quotation. In a nut shell, you can run under rated voltage for fuses but never over.


This is right. So you don't need to worry about the 600VAC fuses in a 208VAC system.

IP: Logged
theogre
Member
Posts: 32520
From: USA
Registered: Mar 99


Feedback score: N/A
Leave feedback





Total ratings: 572
Rate this member

Report this Post06-19-2014 12:52 PM Click Here to See the Profile for theogreClick Here to visit theogre's HomePageSend a Private Message to theogreEdit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by 87antuzzi:
600 volt is fine. The clearing times are the same same and the 600V rating is for the re-strike and insulation ratings. NEC says you can run a 600V gear on a 280V system, ill try to find the quotation. In a nut shell, you can run under rated voltage for fuses but never over.

Yes. "Over volt" fuse is OK.

You'll find this in many cases...
Common to see low volt circuits protected with x Amp 200+ volts fuse.

Simple means Volts rating is stops current up to X volts.

------------------
Dr. Ian Malcolm: Yeah, but your scientists were so preoccupied with whether or not they could, they didn't stop to think if they should.
(Jurassic Park)


The Ogre's Fiero Cave (It's also at the top and bottom of every forum page...)

IP: Logged
Formula88
Member
Posts: 53788
From: Raleigh NC
Registered: Jan 2001


Feedback score: (3)
Leave feedback





Total ratings: 554
Rate this member

Report this Post06-19-2014 12:59 PM Click Here to See the Profile for Formula88Send a Private Message to Formula88Edit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by Lilchief:

I recently started working as a maintenance electrician ...


Are you a licensed electrician? If not, ask the licensed electrician you're working under.
IP: Logged
ray b
Member
Posts: 13466
From: miami
Registered: Jan 2001


Feedback score: N/A
Leave feedback





Total ratings: 325
Rate this member

Report this Post06-19-2014 01:09 PM Click Here to See the Profile for ray bSend a Private Message to ray bEdit/Delete MessageReply w/QuoteDirect Link to This Post
AMPS BLOW FUSES
volts do not
IP: Logged
MidEngineManiac
Member
Posts: 29566
From: Some unacceptable view
Registered: Feb 2007


Feedback score: N/A
Leave feedback





Total ratings: 297
User Banned

Report this Post06-19-2014 01:19 PM Click Here to See the Profile for MidEngineManiacSend a Private Message to MidEngineManiacEdit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by Formula88:


Are you a licensed electrician? If not, ask the licensed electrician you're working under.


YUP !!!-------AND, get whatever he says IN WRITING. Then keep it forever.

I've fought THAT war as a tech manager a FEW times right up to battling the CEO of a comany. They dont like to take "no" for an answer but here at least ANY electrical wrk on a commercial building requires a licenced tradesman (lol, and those cost money )

As soon as ANYTHING ever goes wrong, the lawyers, investigators and everybody else will be hunting for both you (the tech who did the work) and your boss/ manager---and the corporate executive who forced the work will stand there saying "I never told you to do that" and you are hung-OUT-to dry.....if not just hung.

These days, ANYTHING in a tech field is a huge game of CYA.
IP: Logged
PFF
System Bot
Khw
Member
Posts: 11139
From: South Weber, UT. U.S.A.
Registered: Jun 2008


Feedback score: (1)
Leave feedback





Total ratings: 134
Rate this member

Report this Post06-19-2014 01:23 PM Click Here to See the Profile for KhwSend a Private Message to KhwEdit/Delete MessageReply w/QuoteDirect Link to This Post
 
quote
Originally posted by 87antuzzi:


600 volt is fine. The clearing times are the same same and the 600V rating is for the re-strike and insulation ratings. NEC says you can run a 600V gear on a 280V system, ill try to find the quotation. In a nut shell, you can run under rated voltage for fuses but never over.


Yeah when I read the O.P's original post this is what I was going to reply.