Furnace won't ignite--any HVAC experts? by AndyLPhoto
Started on: 09-15-2012 11:22 AM
Replies: 14
Last post by: Khw on 01-12-2013 07:12 PM
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post09-15-2012 11:22 AM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
I have an Intertherm furnace, in a manufactured home. The control card is by Nordyne, and has a single red LED. I know enough to be dangerous, but not really know what I'm doing. I just set the thermostat to give a little heat--first time since about May. When the thermostat kicked in, the startup sequence engaged immediately. The inducer (I think that's what it's called?) starts, and the igniter lights up. There is a big click, and I can feel it in the gas valve like it should be opening. But apparently no gas is being supplied, because it doesn't ignite. Nothing at all visible through the sight glass, other than the igniter shutting down shortly after. It goes through the cycle several times, and then the LED on the control card gives me 4 flashes.

Nordyne Control Card Part #: 624631-A
Intertherm Furnace Model: M3RL080A BW

Any help would be greatly appreciated!

Andy
IP: Logged
PFF
System Bot
James Bond 007
Member
Posts: 8872
From: California.U.S.A.
Registered: Dec 2002


Feedback score: (1)
Leave feedback





Total ratings: 263
Rate this member

Report this Post09-15-2012 11:30 AM Click Here to See the Profile for James Bond 007Send a Private Message to James Bond 007Direct Link to This Post
had a simular problem years ago (diffrent brand furnace). Your Ignightor probubley went out.
IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post09-15-2012 11:50 AM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
Can the igniter be bad if it glows? I replaced an igniter at my last place, but it was totally bad. I found one set of error codes that indicated four was an ignition fault, and to check the igniter.

This one lights up and glows during the startup sequence though.
IP: Logged
Tony Kania
Member
Posts: 20794
From: The Inland Northwest
Registered: Dec 2008


Feedback score:    (7)
Leave feedback





Total ratings: 305
User Banned

Report this Post09-15-2012 11:53 AM Click Here to See the Profile for Tony KaniaSend a Private Message to Tony KaniaDirect Link to This Post
My only input...

If you can get to the igniter, the metal that is connected is more than likey corroded. A bit of emery cloth can save you $80 plus dollars. Not knowing your exact setup, this is my only guess.

Mine needs it every year. Sometimes twice.

Tony
IP: Logged
Tony Kania
Member
Posts: 20794
From: The Inland Northwest
Registered: Dec 2008


Feedback score:    (7)
Leave feedback





Total ratings: 305
User Banned

Report this Post09-15-2012 11:57 AM Click Here to See the Profile for Tony KaniaSend a Private Message to Tony KaniaDirect Link to This Post

Tony Kania

20794 posts
Member since Dec 2008
Yes, an ignitor can glow, but not have enough "glow" to work properly.

Tony
IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post09-15-2012 11:58 AM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
Interesting...it just started going through the cycle again on its own--it must wait a half hour, then try again if there is still a call for heat. First try had the same result, second try it fired up and now it's running. We primarily heat with wood (outdoor furnace) during the winter, but I'd still like to get to the bottom of this. We're at the point now where it's not worth having a fire going, but need occasional heat. The propane furnace also serves as backup during the winter, if the fire goes out.
IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post09-15-2012 11:59 AM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post

AndyLPhoto

2420 posts
Member since Nov 2001
Thanks to both of you for the igniter suggestion. Now that it's running I'm going to let it go, but I'll pull the igniter after it shuts down and get a replacement coming.

EDIT: Interesting that you need one every year. I learned about igniters in our last place when one failed. I figured out the problem and did some reading. It seems like I read the expected lifespan was about 2-3 years? I could be slightly wrong on that--just going from memory. At the time, we had been in the house about 7 years, and had never had it replaced. Not sure how long before that it had been installed, but not bad. I bought an extra and never needed to use it. I pulled the plug on this one (2 wires) and the contacts both looked good.

[This message has been edited by AndyLPhoto (edited 09-15-2012).]

IP: Logged
Raydar
Member
Posts: 41141
From: Carrollton GA. Out in the... country.
Registered: Oct 1999


Feedback score:    (13)
Leave feedback





Total ratings: 461
Rate this member

Report this Post09-15-2012 07:09 PM Click Here to See the Profile for RaydarSend a Private Message to RaydarDirect Link to This Post
Is it possible there was air in the lines?
IP: Logged
Marvin McInnis
Member
Posts: 11599
From: ~ Kansas City, USA
Registered: Apr 2002


Feedback score: N/A
Leave feedback





Total ratings: 227
Rate this member

Report this Post09-15-2012 08:04 PM Click Here to See the Profile for Marvin McInnisClick Here to visit Marvin McInnis's HomePageSend a Private Message to Marvin McInnisDirect Link to This Post
 
quote
Originally posted by Raydar:

Is it possible there was air in the lines?



X2. Seems unlikely, but that would certainly be consistent with the reported symptoms. I wonder if the gas was, by chance, turned off at the meter sometime during the summer.

[This message has been edited by Marvin McInnis (edited 09-15-2012).]

IP: Logged
theogre
Member
Posts: 32520
From: USA
Registered: Mar 99


Feedback score: N/A
Leave feedback





Total ratings: 572
Rate this member

Report this Post09-15-2012 09:05 PM Click Here to See the Profile for theogreClick Here to visit theogre's HomePageSend a Private Message to theogreDirect Link to This Post
Gas is used by what? Stove? Water heater? etc...
If used by anything....
More likely gas solenoid valve has problems.

------------------
Dr. Ian Malcolm: Yeah, but your scientists were so preoccupied with whether or not they could, they didn't stop to think if they should.
(Jurassic Park)


The Ogre's Fiero Cave (It's also at the top and bottom of every forum page...)

IP: Logged
Patrick's Dad
Member
Posts: 5154
From: Weymouth MA USA
Registered: Feb 2000


Feedback score: N/A
Leave feedback





Total ratings: 108
Rate this member

Report this Post09-15-2012 10:47 PM Click Here to See the Profile for Patrick's DadClick Here to visit Patrick's Dad's HomePageSend a Private Message to Patrick's DadDirect Link to This Post
 
quote
Originally posted by theogre:

Gas is used by what? Stove? Water heater? etc...
If used by anything....
More likely gas solenoid valve has problems.



In this line of thinking; is there a sensor/thermocouple of any kind?

My boiler exhibits similar symptoms when the sensing system gets clogged. Soot builds up in a pipe that connects to a sensing device on the boiler. I disconnect the sensor then unscrew it from the pigtail, then I undo the pigtail from the boiler body. I run hot water and poke a cleaner through it until the water stops running black. At that point, I then reassemble it with teflon tape and plug everything back in.
IP: Logged
PFF
System Bot
rogergarrison
Member
Posts: 49601
From: A Western Caribbean Island/ Columbus, Ohio
Registered: Apr 99


Feedback score: N/A
Leave feedback





Total ratings: 551
Rate this member

Report this Post09-16-2012 10:59 AM Click Here to See the Profile for rogergarrisonSend a Private Message to rogergarrisonDirect Link to This Post
I like to cycle anything at least once a month. I turn on my furnaces for a few minutes during the summer, run my mower, generator and weedeater in winter. I run all my cars with a/c a few minutes a month all winter, run my power tops and windows up and down a few times. I usually dont get surprises that way. I rarely let any single car set without a drive for more than a couple weeks.
IP: Logged
theogre
Member
Posts: 32520
From: USA
Registered: Mar 99


Feedback score: N/A
Leave feedback





Total ratings: 572
Rate this member

Report this Post09-16-2012 11:06 AM Click Here to See the Profile for theogreClick Here to visit theogre's HomePageSend a Private Message to theogreDirect Link to This Post
 
quote
Originally posted by Patrick's Dad:
In this line of thinking; is there a sensor/thermocouple of any kind?

His unit uses non pilot ignition.
He had no gas to burn, "sensor" see no fire, system will reset and wait to clear then retry firing.
(wait to clear in case system has gas but still didn't fire, like ignitor or sensor w/ problem.)
IP: Logged
AndyLPhoto
Member
Posts: 2420
From: Skandia, MI, USA
Registered: Nov 2001


Feedback score: N/A
Leave feedback





Total ratings: 97
Rate this member

Report this Post01-12-2013 07:06 PM Click Here to See the Profile for AndyLPhotoClick Here to visit AndyLPhoto's HomePageSend a Private Message to AndyLPhotoDirect Link to This Post
Just remembered about this thread (saw Rodney's furnace thread) and wanted to post a follow-up. I did bring the igniter in and got a generic replacement. It cycled it a few times, and it seemed to work reliably. No long-term results to report, as I started the outdoor wood furnace not too long afterward, so the furnace hasn't been called upon to light up the gas ever since. Thanks again for the advice on the igniter. I love the wealth of knowledge here!
IP: Logged
Khw
Member
Posts: 11139
From: South Weber, UT. U.S.A.
Registered: Jun 2008


Feedback score: (1)
Leave feedback





Total ratings: 134
Rate this member

Report this Post01-12-2013 07:12 PM Click Here to See the Profile for KhwSend a Private Message to KhwDirect Link to This Post
I was going to suggest checking the gas line valve that should be right near the furnace and make sure the gas line was on. I've had that problem before. Thought the gas was on but the furnace wouldn't fire. Start checking things and notice the gas valve was turned off. Now I always check those basics before going any further. We have an autistic son, and with the washer and dryer being in the same room as the furnace and water heater, alot of times he follows my wife in there. It's a knob, he has to turn it...
IP: Logged